Effect of kinematic nonlinearity on pushdown analysis
Dear STKO
I wanted to go back to modeling with asdshellq4 and investigate the effect of geometric nonlinearity on the ultimate load carrying capacity of the structure
I made 2 of the same models changing only the kinematics to corotation A 9x6 m slab with a unit force of q=1 kN/m^2. Displacement control in the midle
Below is the obtained pushdown curve
a) Linear kinematics b) corotational I used the Krylov Newton method. Can you please check if the analysis settings are correct? By setting a different algorithm the procedure ends at the first break of the curve.
I don't understand why there is such a hardening in the case of corotation at the end of the analysis.
Maybe I should use a different algorithm ? or the results obtained are correct ? Corotation introduces additional axial forces, which should increase the maximum load capacity.
2 more technical questions
1. Using MP what can be the maximum number of partitions? As many cores as my processor has?
2. Asd Concrete3D density. When Im modeling in kN/m^3 should te value be 2.5 for concrete?
Best regards
Best regards
Re: Effect of kinematic nonlinearity on pushdown analysis
Google for "Slab catenary action"
I see that the shape of the curve (corotationaL) is similar to the obtianed for example:
https://dr.ntu.edu.sg/bitstream/10356/8 ... itions.pdf
By changing the algorithm to any other (except Krylov), the analyses end with the first displacement jump.
What I don't understand is why there is so much hardening in corotation despite the min max command for steel.
Are you sure that the rebar strain, both in top and bottom bars during the hardening stage, is reached its fracture strain (0.1 as per your model)? If not, the hardening will happen, because, the top bar (initially in compression and during hardening in tension) will now undergo tension under catenary action and provide resistance until it fractures! Please check the strain values.What I don't understand is why there is so much hardening in corotation despite the min max command for steel.
Yes, you can do that.1. Using MP what can be the maximum number of partitions? As many cores as my processor has?
Yes, I assume that the unit weight of concrete is 25 kN/m^3 here.2. Asd Concrete3D density. When Im modeling in kN/m^3 should te value be 2.5 for concrete?
- Capture.PNG (42.55 KiB) Viewed 822 times
Hi, thanks for the feedback,
I made another example but with lower reinforcment, I changed it to fi 10 mm. I pushed the structure to about 2 m. In addition, to increase the clarity of the results, I copied the direction of the 0 and 90 degree reinforcement to the bottom and top reinforcment
Going to the fiber results and check the strain of the top reinforcement reaches it over 0.1 (my min max). I thought the min max command means that in a given time step I exceed the strain value of 0.1 (min max) then in the next time step this value should drop to zero? Simulating the fracture of rebars ?
https://opensees.berkeley.edu/wiki/inde ... x_Material
- strain 2.jpg (198.14 KiB) Viewed 810 times
Yes, that's why you see those progressive load dropsI thought the min max command means that in a given time step I exceed the strain value of 0.1 (min max) then in the next time step this value should drop to zero? Simulating the fracture of rebars ?
I understand, but that is not what I am asking.
I am referring to the results in the MPCO recorder. Why is e11 (or e22) for steel greater than 0.1? Shouldn't there be a zero value in the subsequent time steps after 0.1 is exceeded?
Something like this?:
Hi, the stress becomes zero after reaching the e22=0.1! Not the strain - this will keep on increasing. Please have a look at the materials monotonic response to understand it better.
Exactly, the stress drops to zero (to represent a complete fracture failure), but the strain increases, as the crack opening increases.
Thanks for your help.
Best regards.
Best regards.